LAN-Anbindung für BSB-Bus (Brötje, Elco Thision etc.)

Begonnen von justme1968, 29 November 2014, 19:50:40

Vorheriges Thema - Nächstes Thema

Schotty

So, noch ein Versuch, diesmal auch brav mit zuvor ausgeführtem "6200 Fühler speichern":

11:05:22.996 -> GET /P0 HTTP/1.1

11:05:22.996 -> /P0
11:05:23.228 -> My address: 66
11:05:23.228 -> Destination address: 0
11:05:23.427 -> Duration until answer received: 73
11:05:23.427 -> LAN->HEIZ QUR 6225 Konfiguration -  Gerätefamilie:
11:05:23.460 -> DC C2 00 0B 06 3D 05 00 02 52 88
11:05:23.460 -> HEIZ->LAN ANS 6225 Konfiguration -  Gerätefamilie: 96
11:05:23.493 -> DC 80 42 0E 07 05 3D 00 02 00 00 60 5E 3E
11:05:23.659 -> Duration until answer received: 74
11:05:23.659 -> LAN->HEIZ QUR 6226 Konfiguration -  Gerätevariante:
11:05:23.692 -> DC C2 00 0B 06 3D 05 00 03 42 A9
11:05:23.692 -> HEIZ->LAN ANS 6226 Konfiguration -  Gerätevariante: 100
11:05:23.725 -> DC 80 42 0E 07 05 3D 00 03 00 00 64 68 0E
11:05:23.725 -> Device family: 96
11:05:23.725 -> Device variant: 100
11:05:24.090 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:24.123 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:24.189 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.0 °C
11:05:24.223 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 42 F4 02
11:05:27.276 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:27.309 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:27.375 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.1 °C
11:05:27.409 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 48 55 48
11:05:30.493 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:30.526 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:30.559 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.1 °C
11:05:30.592 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 48 55 48
11:05:32.018 -> GET /8700 HTTP/1.1

11:05:32.018 -> /8700
11:05:32.449 -> Duration until answer received: 74
11:05:32.449 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:05:32.449 -> DC C2 00 0B 06 3D 05 05 21 B9 7C
11:05:32.482 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 12.1 °C
11:05:32.482 -> DC 80 42 0E 07 05 3D 05 21 00 03 06 88 C8
11:05:33.708 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:33.708 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:33.775 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.1 °C
11:05:33.808 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 48 55 48
11:05:36.892 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:36.926 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:36.992 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.0 °C
11:05:36.992 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 42 F4 02
11:05:40.077 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:40.111 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:40.177 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.1 °C
11:05:40.210 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 48 55 48
11:05:42.764 -> Duration until answer received: 72
11:05:42.798 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:05:42.798 -> DC C2 00 0B 06 3D 05 05 21 B9 7C
11:05:42.798 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 12.1 °C
11:05:42.831 -> DC 80 42 0E 07 05 3D 05 21 00 03 06 88 C8
11:05:43.627 -> GET /I10003=17.3 HTTP/1.1

11:05:43.627 -> /I10003=17.3
11:05:43.627 -> set ProgNr 10003 = 17.3
11:05:43.627 -> setting line: 10003 val: 00 04 53
11:05:43.727 -> LAN->HEIZ INF 10003 Benutzerdefiniert -  Außentemperatur: 17.3 °C
11:05:43.760 -> DC C2 00 0E 02 05 00 02 1F 00 04 53 93 EF
11:05:49.430 -> GET /8700 HTTP/1.1

11:05:49.430 -> /8700
11:05:49.828 -> Duration until answer received: 73
11:05:49.828 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:05:49.861 -> DC C2 00 0B 06 3D 05 05 21 B9 7C
11:05:49.861 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 17.3 °C
11:05:49.894 -> DC 80 42 0E 07 05 3D 05 21 00 04 53 1B 0F
11:05:50.292 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:05:50.326 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:05:50.392 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.1 °C
11:05:50.392 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 48 55 48
11:05:54.537 -> GET /10003 HTTP/1.1

11:05:54.537 -> /10003
11:05:54.935 -> Duration until answer received: 73
11:05:54.935 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:05:54.968 -> DC C2 00 0B 06 00 05 02 1F E2 19
11:05:54.968 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: 17.3 °C
11:05:55.001 -> DC 80 42 0E 07 05 00 02 1F 00 04 53 93 A7
11:05:57.487 -> GET /10004 HTTP/1.1

11:05:57.487 -> /10004
11:05:59.277 -> HEIZ->EM1 INF      05040227 00 00 00 00
11:05:59.310 -> DC 80 03 0F 02 05 04 02 27 00 00 00 00 D8 E6
11:06:00.505 -> DISP->HEIZ QUR 8310 Diagnose Erzeuger -  Kesseltemperatur:
11:06:00.505 -> DC 8A 00 0B 06 3D 0D 05 19 4F 8C
11:06:00.571 -> HEIZ->DISP ANS 8310 Diagnose Erzeuger -  Kesseltemperatur: 57.0 °C
11:06:00.604 -> DC 80 0A 0E 07 0D 3D 05 19 00 0E 42 F4 02
11:06:07.409 -> GET /P1 HTTP/1.1

11:06:07.409 -> /P1
11:06:07.674 -> My address: 66
11:06:07.674 -> Destination address: 0
11:06:07.839 -> Duration until answer received: 43
11:06:07.839 -> LAN->HEIZ QUR 6225 Konfiguration -  Gerätefamilie:
11:06:07.873 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 02 F4 F4
11:06:07.873 -> HEIZ->LAN ANS 6225 Konfiguration -  Gerätefamilie: 96
11:06:07.906 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 02 00 00 60 F1 A7
11:06:08.038 -> Duration until answer received: 43
11:06:08.072 -> LAN->HEIZ QUR 6226 Konfiguration -  Gerätevariante:
11:06:08.072 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 03 F4 F5
11:06:08.072 -> HEIZ->LAN ANS 6226 Konfiguration -  Gerätevariante: 100
11:06:08.106 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 03 00 00 64 F1 AC
11:06:08.106 -> Device family: 96
11:06:08.106 -> Device variant: 100
11:06:14.343 -> GET /8700 HTTP/1.1

11:06:14.343 -> /8700
11:06:14.741 -> Duration until answer received: 43
11:06:14.741 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:06:14.774 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:06:14.774 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 17.3 °C
11:06:14.807 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 04 53 F1 C2
11:06:27.680 -> GET /I10003=12.4 HTTP/1.1

11:06:27.680 -> /I10003=12.4
11:06:27.680 -> set ProgNr 10003 = 12.4
11:06:27.680 -> setting line: 10003 val: 00 03 19
11:06:27.779 -> LAN->HEIZ INF 10003 Benutzerdefiniert -  Außentemperatur: 12.4 °C
11:06:27.812 -> 78 11 00 42 C0 02 00 14 02 05 00 02 1F 00 03 19 F1 F4
11:06:30.332 -> HEIZ->ALL  INF      1500022D 00 0E 42
11:06:30.332 -> 78 11 FF 00 CC 02 00 14 02 15 00 02 2D 00 0E 42 F3 0F
11:06:30.697 -> HEIZ->F0 INF      190001FD 00 00 01
11:06:30.730 -> 78 11 F0 00 FC 02 00 14 02 19 00 01 FD 00 00 01 F3 B4
11:06:31.062 -> HEIZ->ALL  INF      191901FE 00 00 01
11:06:31.096 -> 78 11 FF 00 FC 02 00 14 02 19 19 01 FE 00 00 01 F3 DD
11:06:32.388 -> GET /8700 HTTP/1.1

11:06:32.388 -> /8700
11:06:32.786 -> Duration until answer received: 43
11:06:32.819 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:06:32.819 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:06:32.819 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 17.3 °C
11:06:32.852 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 04 53 F1 C2
11:06:39.625 -> HEIZ->ALL  INF      1500020A 00 01 00 01 F4
11:06:39.659 -> 78 13 FF 00 FC 02 00 14 02 15 00 02 0A 00 01 00 01 F4 F1 C6
11:06:43.243 -> Duration until answer received: 43
11:06:43.243 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:06:43.276 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:06:43.276 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 17.3 °C
11:06:43.309 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 04 53 F1 C2
11:06:44.570 -> GET /10003 HTTP/1.1

11:06:44.570 -> /10003
11:06:45.001 -> Duration until answer received: 43
11:06:45.001 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:06:45.035 -> 78 0E 00 42 C0 02 00 14 06 00 05 02 1F F4 D6
11:06:45.035 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: 17.3 °C
11:06:45.068 -> 78 11 42 00 0C 02 00 14 07 05 00 02 1F 00 04 53 F1 80

17.3 via BSB gesetzt, dann Umklemmen&Buswechsel, 12.4 via LPB gesendet, abgefragt: 17.3.
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Also irgendwas muss da noch krumm sein, denn gerade vorher hat es doch mit dem Abfragen von 8700 (bzw. 10004) noch geklappt? Lass die Analge (wenn möglich) vielleicht mal für eine Weile auf LPB, vielleicht auch vorher mal aus- und wieder einschalten. Kann ja sein, dass der schnelle Wechsel ein Grund ist. Vielleicht hat BSB irgendwo intern dann doch Vorrang o.ä., das sollte man ausschließen...
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Schotty

#3887
Zitat von: freetz am 18 Oktober 2019, 11:05:39
...aber mit 10004 kam sie noch zurück - das ist in Deinem Fall die gleiche CommandID wie bei 8700. Also scheint das Setzen doch geklappt zu haben, wenn der Wert danach mit 8700 noch mal zurück kam, und dann auch noch mal nur mit anderer Parameternummer (10004)?
Aber nach 10004 kam doch keine Antwort?!  :o

Zitat
EDIT2: Bei mir kommt bei LPB auch nur "---", wenn ich Parameter 10003 abfrage. Das Setzen klappt aber wie gesagt problemlos...
Das kam bei mir doch nur in dem einen Fall, wo der Regler die Temp ---°C zuvor drin hatte. Wenn ich die AT vorher via BSB setze, kommt sie auch mit 10003 brav zurück. Das Merkwürdige an der Geschichte war doch, dass 8700 die in dem Fall vorher LPB-gesetzte Temp meldete?!

Zitat von: freetz am 18 Oktober 2019, 11:17:15
Also irgendwas muss da noch krumm sein, denn gerade vorher hat es doch mit dem Abfragen von 8700 (bzw. 10004) noch geklappt? Lass die Analge (wenn möglich) vielleicht mal für eine Weile auf LPB, vielleicht auch vorher mal aus- und wieder einschalten. Kann ja sein, dass der schnelle Wechsel ein Grund ist. Vielleicht hat BSB irgendwo intern dann doch Vorrang o.ä., das sollte man ausschließen...
Das hatte ich, siehe Beispiel hier: https://forum.fhem.de/index.php/topic,29762.msg984943.html#msg984943
LPB pur, nix BSB. Nur DORT wird mit 8700 die zuvor gesendete AT angezeigt, aber 10003 zeigt die zuvor im Regler vorhandene ---°C.

Nochmal: Wenn ich eine AT via BSB setze, wird diese unter 8700&10003 und auch im Display angezeigt. Setze ich eine andere Temp via LPB, wird noch immer die via BSB gesetzte Temp angezeigt, sowohl mit 8700 als auch mit 10003 und im Display[/]:

11:27:12.067 -> GET /P1 HTTP/1.1

11:27:12.067 -> /P1
11:27:12.299 -> My address: 66
11:27:12.299 -> Destination address: 0
11:27:12.465 -> Duration until answer received: 43
11:27:12.465 -> LAN->HEIZ QUR 6225 Konfiguration -  Gerätefamilie:
11:27:12.465 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 02 F4 F4
11:27:12.498 -> HEIZ->LAN ANS 6225 Konfiguration -  Gerätefamilie: 96
11:27:12.498 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 02 00 00 60 F1 A7
11:27:12.663 -> Duration until answer received: 43
11:27:12.663 -> LAN->HEIZ QUR 6226 Konfiguration -  Gerätevariante:
11:27:12.663 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 03 F4 F5
11:27:12.697 -> HEIZ->LAN ANS 6226 Konfiguration -  Gerätevariante: 100
11:27:12.697 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 03 00 00 64 F1 AC
11:27:12.697 -> Device family: 96
11:27:12.730 -> Device variant: 100
11:27:16.178 -> GET /8700 HTTP/1.1

11:27:16.178 -> /8700
11:27:16.576 -> Duration until answer received: 43
11:27:16.576 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:27:16.609 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:27:16.609 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: --- °C
11:27:16.642 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 01 00 00 F1 6C
11:27:24.435 -> GET /10003 HTTP/1.1

11:27:24.435 -> /10003
11:27:24.833 -> Duration until answer received: 43
11:27:24.833 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:27:24.866 -> 78 0E 00 42 C0 02 00 14 06 00 05 02 1F F4 D6
11:27:24.866 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: --- °C
11:27:24.899 -> 78 11 42 00 0C 02 00 14 07 05 00 02 1F 01 00 00 F1 2A
11:27:29.408 -> HEIZ->ALL  INF      0500006B 0A 06
11:27:29.442 -> 78 10 FF 00 FC 02 00 14 02 05 00 00 6B 0A 06 F4 29
11:27:29.641 -> HEIZ->ALL  INF      1500022D 00 0E 48
11:27:29.674 -> 78 11 FF 00 CC 02 00 14 02 15 00 02 2D 00 0E 48 F3 15
11:27:30.736 -> HEIZ->F0 INF      190001FD 00 00 01
11:27:30.769 -> 78 11 F0 00 FC 02 00 14 02 19 00 01 FD 00 00 01 F3 B4
11:27:31.100 -> HEIZ->ALL  INF      191901FE 00 00 01
11:27:31.100 -> 78 11 FF 00 FC 02 00 14 02 19 19 01 FE 00 00 01 F3 DD
11:27:36.042 -> GET /I10003=13.2 HTTP/1.1

11:27:36.042 -> /I10003=13.2
11:27:36.042 -> set ProgNr 10003 = 13.2
11:27:36.042 -> setting line: 10003 val: 00 03 4C
11:27:36.142 -> LAN->HEIZ INF 10003 Benutzerdefiniert -  Außentemperatur: 13.2 °C
11:27:36.175 -> 78 11 00 42 C0 02 00 14 02 05 00 02 1F 00 03 4C F2 27
11:27:40.023 -> HEIZ->ALL  INF      1500020A 00 01 00 01 F4
11:27:40.056 -> 78 13 FF 00 FC 02 00 14 02 15 00 02 0A 00 01 00 01 F4 F1 C6
11:27:42.776 -> GET /8700 HTTP/1.1

11:27:42.776 -> /8700
11:27:43.141 -> Duration until answer received: 43
11:27:43.141 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:27:43.174 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:27:43.174 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 13.2 °C
11:27:43.207 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 4C F1 BA
11:27:47.950 -> GET /10003 HTTP/1.1

11:27:47.950 -> /10003
11:27:48.348 -> Duration until answer received: 43
11:27:48.348 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:27:48.381 -> 78 0E 00 42 C0 02 00 14 06 00 05 02 1F F4 D6
11:27:48.381 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: --- °C
11:27:48.414 -> 78 11 42 00 0C 02 00 14 07 05 00 02 1F 01 00 00 F1 2A
11:27:48.613 -> Duration until answer received: 43
11:27:48.613 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:27:48.613 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:27:48.646 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 13.2 °C
11:27:48.646 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 4C F1 BA
11:27:49.242 -> HEIZ->ALL  INF      0500006B 00 00
11:27:49.276 -> 78 10 FF 00 FC 02 00 14 02 05 00 00 6B 00 00 F4 19
11:28:23.224 -> GET /P0 HTTP/1.1

11:28:23.224 -> /P0
11:28:23.456 -> My address: 66
11:28:23.456 -> Destination address: 0
11:28:23.655 -> Duration until answer received: 73
11:28:23.655 -> LAN->HEIZ QUR 6225 Konfiguration -  Gerätefamilie:
11:28:23.688 -> DC C2 00 0B 06 3D 05 00 02 52 88
11:28:23.688 -> HEIZ->LAN ANS 6225 Konfiguration -  Gerätefamilie: 96
11:28:23.721 -> DC 80 42 0E 07 05 3D 00 02 00 00 60 5E 3E
11:28:23.887 -> Duration until answer received: 72
11:28:23.887 -> LAN->HEIZ QUR 6226 Konfiguration -  Gerätevariante:
11:28:23.920 -> DC C2 00 0B 06 3D 05 00 03 42 A9
11:28:23.920 -> HEIZ->LAN ANS 6226 Konfiguration -  Gerätevariante: 100
11:28:23.953 -> DC 80 42 0E 07 05 3D 00 03 00 00 64 68 0E
11:28:23.953 -> Device family: 96
11:28:23.953 -> Device variant: 100
11:28:30.719 -> DISP->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:28:30.752 -> DC 8A 00 0B 06 3D 05 05 21 51 76
11:28:30.819 -> HEIZ->DISP ANS 8700 Diagnose Verbraucher -  Außentemperatur: 13.2 °C
11:28:30.852 -> DC 80 0A 0E 07 05 3D 05 21 00 03 4C 59 17
11:28:33.506 -> GET /I10003=14.5 HTTP/1.1

11:28:33.506 -> /I10003=14.5
11:28:33.506 -> set ProgNr 10003 = 14.5
11:28:33.506 -> setting line: 10003 val: 00 03 A0
11:28:33.572 -> LAN->HEIZ INF 10003 Benutzerdefiniert -  Außentemperatur: 14.5 °C
11:28:33.606 -> DC C2 00 0E 02 05 00 02 1F 00 03 A0 D5 04
11:28:40.907 -> DISP->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:28:40.940 -> DC 8A 00 0B 06 3D 05 05 21 51 76
11:28:41.006 -> HEIZ->DISP ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:28:41.006 -> DC 80 0A 0E 07 05 3D 05 21 00 03 A0 65 B5
11:28:48.504 -> Duration until answer received: 74
11:28:48.504 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:28:48.537 -> DC C2 00 0B 06 3D 05 05 21 B9 7C
11:28:48.537 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:28:48.570 -> DC 80 42 0E 07 05 3D 05 21 00 03 A0 5D E4
11:28:48.802 -> GET /8700/10003 HTTP/1.1

11:28:48.802 -> /8700/10003
11:28:49.200 -> Duration until answer received: 72
11:28:49.200 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:28:49.233 -> DC C2 00 0B 06 3D 05 05 21 B9 7C
11:28:49.233 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:28:49.266 -> DC 80 42 0E 07 05 3D 05 21 00 03 A0 5D E4
11:28:49.498 -> Duration until answer received: 74
11:28:49.498 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:28:49.531 -> DC C2 00 0B 06 00 05 02 1F E2 19
11:28:49.531 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: 14.5 °C
11:28:49.531 -> DC 80 42 0E 07 05 00 02 1F 00 03 A0 D5 4C
11:28:51.123 -> DISP->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:28:51.156 -> DC 8A 00 0B 06 3D 05 05 21 51 76
11:28:51.222 -> HEIZ->DISP ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:28:51.255 -> DC 80 0A 0E 07 05 3D 05 21 00 03 A0 65 B5
11:29:00.611 -> GET /P1 HTTP/1.1

11:29:00.611 -> /P1
11:29:00.876 -> My address: 66
11:29:00.876 -> Destination address: 0
11:29:01.042 -> Duration until answer received: 43
11:29:01.042 -> LAN->HEIZ QUR 6225 Konfiguration -  Gerätefamilie:
11:29:01.075 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 02 F4 F4
11:29:01.075 -> HEIZ->LAN ANS 6225 Konfiguration -  Gerätefamilie: 96
11:29:01.075 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 02 00 00 60 F1 A7
11:29:01.241 -> Duration until answer received: 43
11:29:01.274 -> LAN->HEIZ QUR 6226 Konfiguration -  Gerätevariante:
11:29:01.274 -> 78 0E 00 42 C0 02 00 14 06 3D 05 00 03 F4 F5
11:29:01.274 -> HEIZ->LAN ANS 6226 Konfiguration -  Gerätevariante: 100
11:29:01.307 -> 78 11 42 00 0C 02 00 14 07 05 3D 00 03 00 00 64 F1 AC
11:29:01.307 -> Device family: 96
11:29:01.307 -> Device variant: 100
11:29:15.077 -> GET /I10003=17.1 HTTP/1.1

11:29:15.077 -> /I10003=17.1
11:29:15.077 -> set ProgNr 10003 = 17.1
11:29:15.077 -> setting line: 10003 val: 00 04 46
11:29:15.176 -> LAN->HEIZ INF 10003 Benutzerdefiniert -  Außentemperatur: 17.1 °C
11:29:15.209 -> 78 11 00 42 C0 02 00 14 02 05 00 02 1F 00 04 46 F2 22
11:29:20.187 -> HEIZ->ALL  INF    0 Uhrzeit und Datum -  Datum/Zeit: 04.01.2004 00:48:25
11:29:20.221 -> 78 17 FF 00 FC 02 00 14 02 05 00 00 6C 00 68 01 04 07 00 30 19 00 ED E5
11:29:28.986 -> HEIZ->ALL  INF      191901FE 00 00 01
11:29:29.019 -> 78 11 FF 00 FC 02 00 14 02 19 19 01 FE 00 00 01 F3 DD
11:29:30.413 -> HEIZ->ALL  INF      1500022D 00 0E 42
11:29:30.447 -> 78 11 FF 00 CC 02 00 14 02 15 00 02 2D 00 0E 42 F3 0F
11:29:30.779 -> HEIZ->F0 INF      190001FD 00 00 01
11:29:30.812 -> 78 11 F0 00 FC 02 00 14 02 19 00 01 FD 00 00 01 F3 B4
11:29:40.040 -> HEIZ->ALL  INF      1500020A 00 01 00 01 F4
11:29:40.074 -> 78 13 FF 00 FC 02 00 14 02 15 00 02 0A 00 01 00 01 F4 F1 C6
11:29:48.833 -> Duration until answer received: 43
11:29:48.833 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:29:48.867 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:29:48.867 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:29:48.900 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 A0 F2 0E
11:29:49.927 -> GET /8700/10003 HTTP/1.1

11:29:49.927 -> /8700/10003
11:29:50.326 -> Duration until answer received: 43
11:29:50.326 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
11:29:50.359 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
11:29:50.359 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 14.5 °C
11:29:50.392 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 A0 F2 0E
11:29:50.558 -> Duration until answer received: 43
11:29:50.558 -> LAN->HEIZ QUR 10003 Benutzerdefiniert -  Außentemperatur:
11:29:50.591 -> 78 0E 00 42 C0 02 00 14 06 00 05 02 1F F4 D6
11:29:50.591 -> HEIZ->LAN ANS 10003 Benutzerdefiniert -  Außentemperatur: 14.5 °C
11:29:50.624 -> 78 11 42 00 0C 02 00 14 07 05 00 02 1F 00 03 A0 F1 CC

Hierbei habe ich mir zusätzlich die Temp im Display anzeigen lassen: Die via LPB gesetzten 17.1° werden nicht angezeigt (auch nicht nach >5min), es bleibt immer bei den 14.5 via BSB. Lediglich die anfangs via LPB gesendeten 13.2° wurden im Display angezeigt, als zuvor aber kein Wert vorlag, also ---°C.
Warum diesmal übrigens die DISP->HEIZ-Meldungen nicht ständig kommen, weiß ich nicht. Vielleicht ist ja bei meinem Testsystem irgendwas kaputt  ::) Wenn ich das SSR-Testsystem wieder habe, dann teste ich damit auch alles nochmal.
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Bzgl. 10004: Doch, da kam eine Antwort, und zwar auch mit den 12.1 Grad:

10:58:39.732 -> /10004
10:58:40.030 -> HEIZ->ALL  INF      1500020A 00 01 00 01 F4
10:58:40.063 -> 78 13 FF 00 FC 02 00 14 02 15 00 02 0A 00 01 00 01 F4 F1 C6
10:58:41.588 -> Duration until answer received: 43
10:58:41.588 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
10:58:41.622 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
10:58:41.622 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 12.1 °C
10:58:41.655 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 06 F1 74

Oben steht die 10004 und säter dann die 8700, aber das nur, weil 10004 und 8700 die gleiche CommandID haben und die 8700 zuerst gefunden wird. Deswegen meinte ich ja, dass es bei dem Szenario mit dem Setzen und Abfragen geklappt hat - nur eben nicht das Abfragen über die 10003. Das kann aber auch gut so sein, denn bei Dir (und anderen) ist die Abfrage der AT (053D0521) eine andere CommandID als das Setzen (0500021F).

Ob mit LPB was bei der 10003 zurück kommt, wenn vorher mit BSB etwas gesetzt wurde, würde ich jetzt mal außen vor lassen, keine Ahnung, wie die Therme da vorgeht, vielleicht ist der Fall auch einfach gar nicht getestet worden und das ist halt eine Anomalie. Wie gesagt, den fliegenden Wechsel zwischen LPB und BSB würde ich - was diesen Test jetzt angeht - vermeiden.

Wenn also bei einem "beruhigten" LPB-System die AT via I10003 gesetzt und per 8700 abgefragt werden kann, dann funktioniert das Setzen als solches. Welche Rückmeldungen auf 10003 und 10004 kommen, ist da (erst mal) irrelevant, das war bisher ja auch nur eine Vermutung meinerseits, dass das zu eindeutigen Ergenissen führt, was es anscheienend nicht tut...
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Schotty

Zitat von: freetz am 18 Oktober 2019, 11:50:34
Bzgl. 10004: Doch, da kam eine Antwort, und zwar auch mit den 12.1 Grad:

10:58:39.732 -> /10004
10:58:40.030 -> HEIZ->ALL  INF      1500020A 00 01 00 01 F4
10:58:40.063 -> 78 13 FF 00 FC 02 00 14 02 15 00 02 0A 00 01 00 01 F4 F1 C6
10:58:41.588 -> Duration until answer received: 43
10:58:41.588 -> LAN->HEIZ QUR 8700 Diagnose Verbraucher -  Außentemperatur:
10:58:41.622 -> 78 0E 00 42 C0 02 00 14 06 3D 05 05 21 F5 18
10:58:41.622 -> HEIZ->LAN ANS 8700 Diagnose Verbraucher -  Außentemperatur: 12.1 °C
10:58:41.655 -> 78 11 42 00 0C 02 00 14 07 05 3D 05 21 00 03 06 F1 74

Oben steht die 10004 und säter dann die 8700, aber das nur, weil 10004 und 8700 die gleiche CommandID haben und die 8700 zuerst gefunden wird.
Da dachte ich, dass die 8700er von der Duchschnittsberechnungsabfrage des Adapters kam, aber ok.

Zitat
Deswegen meinte ich ja, dass es bei dem Szenario mit dem Setzen und Abfragen geklappt hat - nur eben nicht das Abfragen über die 10003.
...
Wenn also bei einem "beruhigten" LPB-System die AT via I10003 gesetzt und per 8700 abgefragt werden kann, dann funktioniert das Setzen als solches.
Aber wie gesagt nur in dem einen Fall, bei der Regler vorher GAR KEINEN Wert hatte und ---°C anzeigte. Siehe mein letzter Beitrag, da wird sogar am heizungsseitigen Display die via LPB gesetzte Temp nicht angezeigt, wenn zuvor ein Wert vorlag. Gerade nochmal getestet.
Mir kommt es so vor, als wenn der LPB-Wert nur dann übernommen wird, wenn zuvor im Regler kein Wert vorhanden war (---°C), frei nach dem Motto 'besser als gar nichts'.
Aber gut, belassen wir's dabei..
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Das kann auch sein, dass der von der Durchschnittsberechnung her kam, aber nichtsdestotrotz liefert er doch den richtigen Wert, oder?

Was passiert denn, wenn Du auf ein "---" hin per LPB einen Wert setzt und dann einen anderen Wert (wieder per LPB) setzt? Wenn es so ist, dass die Anlage nur dann einen Wert akzeptiert, wenn vorher "---" war, dürfte der zweite Wert ja nicht gespeichert werden. Wenn er gespeichert wird, kann es sein, dass Deine Anlage (ob nun von den Entwicklern so beabsichtigt oder nicht) BSB eine Priorität einräumt. Macht ja auch Sinn, da es die Funkgeräte ja nicht für LPB gibt. Trotzdem wäre es ja gut zu wissen, dass es über LPB trotzdem geht, dann aber möglicherweise nur unter der Voraussetzung, die Du jetzt herausgefunden hast, nämlich, dass ein etwaig vorher angeschlossenener BSB-Funkempfänger aus dem System entfernt worden sein muss.
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Schotty

#3891
Zitat von: freetz am 18 Oktober 2019, 12:18:35
Was passiert denn, wenn Du auf ein "---" hin per LPB einen Wert setzt und dann einen anderen Wert (wieder per LPB) setzt? Wenn es so ist, dass die Anlage nur dann einen Wert akzeptiert, wenn vorher "---" war, dürfte der zweite Wert ja nicht gespeichert werden.
Ja, wird angenommen.

Zitat
Macht ja auch Sinn, da es die Funkgeräte ja nicht für LPB gibt.
Also wenn ich mich jetzt nicht komplett irre, dann hatte ich doch damals (vor etlichen Seiten hier im Thread) die ganzen Anschlüsse mal durchgemessen. Dabei kam doch u.a. raus, dass
1. BSB&LPB eine gemeinsame Masse haben und
2. von X60 irgendein Pin mit LPB verbunden war. Dabei kommt mir auch gerade wieder das kürzlich erwähnte ModBus-Modul in den Sinn, dessen Signale als LPB-Befehle gewertet werden. Der Funkempfänger FEK (der, den Jewe auch in Betrieb hat) wird ja an X60 angeschlossen - eventuell geht die Kommunikation da dann auch über den LPB?! Anyway..
3. Nachtrag: ..irgendwie gabs da aber auch eine Verbindung zwischen MB und CL+, allerdings nur in eine Stromflussrichtung..irgendwas ist mir da zumindest im Hinterkopf geblieben..aber wenn bei dir der gleichzeitige Anschluss an BSB&LPB keine Probleme macht, ists ja gut.

Zitat
Trotzdem wäre es ja gut zu wissen, dass es über LPB trotzdem geht, dann aber möglicherweise nur unter der Voraussetzung, die Du jetzt herausgefunden hast, nämlich, dass ein etwaig vorher angeschlossenener BSB-Funkempfänger aus dem System entfernt worden sein muss.
Wobei man dann vermutlich die AT-Funktion eh nicht benutzt, aber egal. Wenn generell ein AT-Fühler angeschlossen ist, scheinen (laut tetzlav's Log) die Temps sowieso in so kurzen Intervallen zu kommen, dass nichts anderes angenommen wird/werden kann. Oder alles andere wird ganz einfach ignoriert. Egal ob über BSB oder LPB (gerade auch nochmal getestet mit direkt nachfolgender 8700-Abfrage), da passiert nüscht.
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

Schotty

Hast du denn eigtl bei deinem ZR1 mal mein Szenario durchgespielt? Also über BSB setzen, abfragen, umklemmen auf LPB, neu setzen, abfragen etc?
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Zitat von: Schotty am 18 Oktober 2019, 12:07:29
Aber gut, belassen wir's dabei..
Zitat von: Schotty am 18 Oktober 2019, 12:41:56
Anyway..
Zitat von: Schotty am 18 Oktober 2019, 12:41:56
aber egal.

Sorry, ich will Dich damit nicht nerven, und wenn Du meinst, dass es keinen Sinn macht, der Sache auf den Grund zu gehen oder gerade keine Zeit hast, ist das auch völlig in Ordnung. Ich denke halt, dass es gut ist, jetzt, wo man gerade an der Sache dran ist, die möglichen Einschränkungen zu kennen, als wenn man dann in ein paar Dutzend Seiten später danach von einem Neuling gefragt wird. Und ja, vielleicht wird jemand der einen Funk-Empfänger hat, nicht unbedingt auf die BSB-LAN-Variante umsteigen - oder wie tetzlav dann eben doch. Ich persönlich hätte diese Möglichkeit für meine Arbeitswohnung sehr gerne, denn da habe ich eine Etagenheizung in der Wohnung, die aber ohne Außentemperaturfühler betrieben wird. Blöd, dass das Teil mit eBus läuft und es da anscheinend nicht so einfach ist, die AT zu simulieren.

Und was das ZR1 angeht: Da kann ich BSB-LAN zeitgleich an BSB und LPB anschließen und mit /P hin und her schalten und die Temperaturwerte werden immer übernommen. Aber wie gesagt eben auch über reines LPB, ohne dass vorher etwas gesetzt wurde...
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

freetz

Was X60 (ist das auch der Anschluss für das OCI420?) und LPB etc. angeht, wäre das in der Tat interessant, ob da "echtes" LPB an die Platine gesendet wird oder (wie ich das beim OCI420 vermute) die jeweiligen Bus-Signale auf interne Signale der Platine umgesetzt werden (weshalb die Abfrage beim OCI420 ja so viel länger dauert, als direkt über BSB/LPB). Wenn da nicht nur Masse, sondern ein Datenpfad ist, müsste man den Funkempfänger von Jewe über die beiden Adern (also Masse und Daten) auch direkt an BSB-LAN anschließen und abfragen können. Aber das hätte für uns jetzt funktional keine Relevanz, außer, dass man den Bus noch besser verstehen würde...
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Schotty

#3895
Zitat von: freetz am 18 Oktober 2019, 12:50:56
Sorry, ich will Dich damit nicht nerven, und wenn Du meinst, dass es keinen Sinn macht, der Sache auf den Grund zu gehen
Wieso nerven? :o Da hast du was missverstanden - ich versuche doch, der Sache auf den Grund zu gehen!?!
Ich persönlich finde nur das von mir beobachtete und reproduzierbare Verhalten des Reglers einfach sehr merkwürdig und gleichzeitig interessant - vielleicht ist das Verhalten aber auch gar nicht so relevant, da die AT letztlich ja sowieso nur über LPB oder BSB allein gesendet werden wird.
Wenn das beobachtete Verhalten kein Indiz dafür ist, dass die Temperaturübermittlung via LPB unzuverlässig ist (und so hatte ich es für mich interpretiert), dann ist ja gut. Darauf war das "Aber gut, belassen wir's dabei" bezogen.

Selbstverständlich ist das Feature hochinteressant, das habe ich von Anfang an betont und asap getestet - das Handbuchkap ist ja auch schon (fast) fertig ;)

Zitat
Und was das ZR1 angeht: Da kann ich BSB-LAN zeitgleich an BSB und LPB anschließen und mit /P hin und her schalten und die Temperaturwerte werden immer übernommen. Aber wie gesagt eben auch über reines LPB, ohne dass vorher etwas gesetzt wurde...
Also wird der vorher via BSB gesendete AT-Wert dann via LPB überschrieben und auch angezeigt? Ok, also DAS finde ich dann aber wieder richtig ominös, das ist ja gerade das, was bei mir nicht funktioniert.

Nein, das OCI420 wird bei den LM-Reglern an X40 angeschlossen (X60 gibt's bei denen glaube ich gar nicht (nur bei RVS)).
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Na dann ist ja alles gut :).
Und klar ist es ein Indiz dafür, dass die Temperaturübermittlung "unzuverlässig" ist, in dem Sinne, dass es bei manchen Reglern eben Probleme beim (eher unwahrscheinlichen) Parallelbetrieb von BSB und LPB gibt. Gleichzeitig ist die Möglichkeit des Parallelbetriebs ja eine, die ich heute morgen erst herausgefunden habe, und die ja auch Sinn machen kann. Insofern ist die Erkenntnis, dass es nicht bei allen Reglern reibungslos läuft, wichtig, aber ebenso wichtig ist es eben herauszufinden, dass es auch bei denen trotzdem "LPB-standalone" funktioniert. Und das scheint nach Deinem letzten Test ja klar zu sein, wo Du ja mehrfach Werte schreiben konntest.

Und ja, bei mir funktioniert das Hin- und Herüberschreiben der AT über BSB und LPB problemlos, deswegen hat's mich ja gewundert, dass das bei Deinem Regler dann doch anders ist - aber das ist ja eh' schon eine ältere Erkenntnis, dass es trotz vieler Ähnlichkeiten dann doch immer wieder Unterschiede gibt, die man sich nicht wirklich erklären kann...
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Schotty

#3897
Zitat von: freetz am 18 Oktober 2019, 13:24:30
Probleme beim (eher unwahrscheinlichen) Parallelbetrieb von BSB und LPB gibt. Gleichzeitig ist die Möglichkeit des Parallelbetriebs ja eine, die ich heute morgen erst herausgefunden habe, und die ja auch Sinn machen kann.
Wobei du mit 'Parallelbetrieb' in diesem Fall den gleichzeitigen Anschluss des Adapters an beiden Bussen (? ..mit nur einem >s< wollte ich es aber gerade auch nicht schreiben.. ;D ) meinst - nicht zu verwechseln mit der gleichzeitigen Nutzung von BSB und LPB per se, bspw wenn ein LPB-Verbund zweier Regler vorliegt. Richtig?

EDIT: Denn 'parallel' in dem Sinne habe ich es ja auch nicht probiert, ich habe ja ebenfalls mit /P gewechselt und sogar hardwareseitig den Anschluss geändert.
Handbuch zur BSB-LAN Hard- & Software (Anbindung v. Heizungsreglern, u.a. von Brötje & Elco):
https://1coderookie.github.io/BSB-LPB-LAN/

freetz

Der "parallele" Betrieb ist im Endeffekt nichts anderes, als wenn man die Stecker manuell wechseln würde, denn die Daten, die das jeweils andere System sieht, "versteht" es nicht und ignoriert es einfach, ähnlich wie bei den Usern, wo die vor längerer Zeit wegen der Taktabweichung von den Thermen keine Antwort bekamen.
Dieser "Parallelbetrieb" (der eigentlich sequentiell ist) hat halt nur den Vorteil, dass man softwareseitig mit /P zwischen den Bussen wechseln kann, um Funktionen zu nutzen, die der jeweils andere Bus nicht zur Verfügung stellt (wie bei mir mit dem OCI420 über LPB z.B.), ohne, dass man die die Anschlüsse hardwareseitig wechseln müsste.
Demzufolge brauchst Du es jetzt auch nicht auf diese Weise probieren, denn für die Nutzung ist es das Gleiche, wie wenn Du mit hardwareseitig den Anschluss änderst und dann mit /P umschaltest.
Alle Infos zur Anbindung von Heizungssystemen mit PPS-, LPB- bzw. BSB-Bus ans LAN gibt es hier:
https://github.com/fredlcore/bsb_lan

Alle Infos zum WLAN-Interface "Robotan" für Ambrogio/Stiga/Wolf und baugleiche Rasenmähroboter:
https://github.com/fredlcore/robotan

Maista

Hallo zusammen,

Zitat von: Schotty am 17 Oktober 2019, 19:56:18
@Maista: Sehr gut ;) Dann könntest du nach dem nächsten Update doch bitte mal /10003 abrufen und sehen, ob die AT gemeldet wird, dann haben wir das für den LMS14 auch schonmal geklärt.

Bzgl Laufzeit hattest du meine Antwort auf deine PN gesehen, oder?

Ich fahre morgen Richtung Norden. Keine Ahnung wann ich danach dazu komme.
Muss mich dann erst wieder einlesen. Es ging die letzten Monate ja doch etwas an der Software.

Ulf, deine Mail kam an, ich hatte nur gedacht das freetz doch irgend wo die Laufzeit stehen hat oder zumindest es einbauen will.  ;)
So hab ich kein Plan was die Büchse im Keller treibt ;).

@freetz
Schade das es es keine Laufzeit gibt, den Log auf SD habe ich deaktiviert da ich mit FHEM die Daten logge.
Aber wenn das nach 44 Tagen wieder überschrieben wird nutzt das nichts um zu sehen wann es ein Problem gibt.

Nächste Woche komme ich irgend wann zurück, eventl. ergibt sich Zeit für FHEM.

Bis dahin, schönes Wochenende.

Gerd