Hallo zusammen,
wie kann ich die u.g. Fehler beseitigen?
TF = Temperaturfühler EQ3 HomeMatic Funk Wandthermostat 132030
TK = Türkontakt EQ3 HomeMatic Funk Tür / Fensterkontakt optisch 130297
configCheck done:
missing register list
41.wz.TK.Balkontuer: RegL_00:
peer not verified. Check that peer is set on both sides
41.wz.TF.WindowRec p:41.wz.TK.Balkontuer
PairedTo mismatch to IODev
41.wz.TK.Balkontuer paired:0x000000 IO attr: 2BAA92.
templist mismatch
41.ez.HZ.Clima: file: ./tempList.cfg for 41.ez.HZ.Clima does not exist
41.mz.HZ.Clima: file: ./tempList.cfg for 41.mz.HZ.Clima does not exist
41.sz.HZ.Clima: file: ./tempList.cfg for 41.sz.HZ.Clima does not exist
41.wz.HZ.Clima: file: ./tempList.cfg for 41.wz.HZ.Clima does not exist
44.ez.HZ.Clima: file: ./tempList.cfg for 44.ez.HZ.Clima does not exist
44.sz.HZ.Clima: file: ./tempList.cfg for 44.sz.HZ.Clima does not exist
44.wz.HZ.Clima: file: ./tempList.cfg for 44.wz.HZ.Clima does not exist
41.wz.TF.Climate: file: ./tempList.cfg for 41.wz.TF.Climate does not exist
Hi,
Hast du bei beiden Geräten mal ein getConfig durchgeführt?
Zur Templist sollte es ein Attribut geben tempListTmpl welches du auf 0, bzw. In aktuellen verdienen auf None setzen kannst, dann sollte das nicht mehr kommen
für den templist "fehler" würde ich einfach in hminfo ein set hminfo templist save machen. dann hast du das templistfile mit allen templist der thermostate für eventuelle fälle liegen und der "fehler" ist auch weg